I was going to post in the hazardous location group, but this seems more like a control design question.
So I have a design with a fuel pump. My initial design included a remote Estop button as required by the NEC. The Estop has to disconnect any hot wires, and also any neutral wires (per the 2020 NEC), so my initial design included contactors.
It was pretty simple - the normally closed Estop button would drop out the contactors when pressed, and the contactors would open both the hot and neutral wires.
But now I see another requirement - the pumps are unattended, so I also need an Estop button at the pumps. The problem is, this button must also have any hot wires and neutral wires disconnected when pressed.
First I though no problem, I'll just show the estops wired through the same contactors they shut off. Then I realized there isn't any way to reset this. The estop buttons wouldn't be energized until relay is energized, and the relay won't be energized until the estop buttons are.
So I started thinking about using a shunt trip circuit breaker. But that won't shunt trip a neutral wire.
So now I'm thinking a shunt trip for the hot wires and a contactor for the neutral. But I hate having a relay that only opens the netural wire - it seems kind of dangerous since having the relay open could allow the neutral wire to be energized with 120 volts all the way from the pumps back to the contactor.
I feel like this is becoming really over complex, and i must be re-inventing the wheel somehow.
But I can't seem to find a simpler solution.
So I have a design with a fuel pump. My initial design included a remote Estop button as required by the NEC. The Estop has to disconnect any hot wires, and also any neutral wires (per the 2020 NEC), so my initial design included contactors.
It was pretty simple - the normally closed Estop button would drop out the contactors when pressed, and the contactors would open both the hot and neutral wires.
But now I see another requirement - the pumps are unattended, so I also need an Estop button at the pumps. The problem is, this button must also have any hot wires and neutral wires disconnected when pressed.
First I though no problem, I'll just show the estops wired through the same contactors they shut off. Then I realized there isn't any way to reset this. The estop buttons wouldn't be energized until relay is energized, and the relay won't be energized until the estop buttons are.
So I started thinking about using a shunt trip circuit breaker. But that won't shunt trip a neutral wire.
So now I'm thinking a shunt trip for the hot wires and a contactor for the neutral. But I hate having a relay that only opens the netural wire - it seems kind of dangerous since having the relay open could allow the neutral wire to be energized with 120 volts all the way from the pumps back to the contactor.
I feel like this is becoming really over complex, and i must be re-inventing the wheel somehow.
But I can't seem to find a simpler solution.