Full Size EGC

Status
Not open for further replies.
Without know the circuit ampacity no one can say for sure if the EGC in the photo is larger than required or not. A 30 amp receptacle would have a full size EGC even if the ungrounded conductors were #6 AWG.
 
I follow the general rule that field-installed conductors need to be bushed, factory-installed don't.

Then there's AC/BX. :rolleyes:
 