kpepin
I was wondering if there is any advantage to using a full size equipment grounding conductor. The reason I am asking is because the project I am working on specifies the same size EGC as the Current Carrying Conductors. For example, one panel we are feeding is a 600A 480/277 Panel and the plan shows 2 parallel sets of 350 MCM with a 350 MCM EGC (5 350MCM total in each 3" EMT). I was just wondering what kind of benefit this has when the NEC allows a #1 EGC.
A little background to the project: A High School Addition, each 480V panel feeds a 208/120V panel (through transformers) - each containing a lot of Isolated ground receptacle circuits.