I am a commercial contractor who builds municipal pools when available. On a current project we have a situation were the concrete contractor incorrectly placed some "wet stuck" rebar stirrups. These bars are not tied to the rebar mats which are bonded. The intent was to bond these bars with a bare #8 copper. Unfortunately the architect & engineer came up with a rework for the bars which called for them to be cut off flush with the concrete. This was done, now they tell us that the encased rebar stubs must be bonded or removed. My electrical contractor tells me that drilling into the exposed top of the cut-off bar with a self-drilling self-tapping screw and attaching a bonding clip will not meet code. Drilling the bars out of the concrete could cuase damage to other rebar.
The big question is basically, since these #4 rebar stubs are to be subsequently buried in concrete is bonding actually required by code?
Thanks
[ May 19, 2004, 11:34 AM: Message edited by: don_resqcapt19 ]
The big question is basically, since these #4 rebar stubs are to be subsequently buried in concrete is bonding actually required by code?
Thanks