Hi
I have a commercial space, a warehouse under major remodeling and has a 800A, 3 phase 4-wire service.
Available fault by local utility company is 27,000A
we installed four sub panels throughout the space with breakers at 10,000 AIC.
now the inspector wants the AIC of new brkrs in the sub panel to be matched with available fault.
What do think the is the best approch to make a fully rating.... if my short circuit calcs showes 13000-14000 fault at those new breakers?
Thanx