Designer69
Senior Member
the reason I posted this question is because I got confused with current consumption of a simple heater.
the heater is rated 500W at 240VAC but they changed the connected voltage to 120VAC and said the current will reduce essentially in half. Also, only half the rated power of the heater will be produced.
I was initially thinking current would double because it's still going to try to produce 500W but I guess if the power output gets reduced then current would too.
the heater is rated 500W at 240VAC but they changed the connected voltage to 120VAC and said the current will reduce essentially in half. Also, only half the rated power of the heater will be produced.
I was initially thinking current would double because it's still going to try to produce 500W but I guess if the power output gets reduced then current would too.