I the VFD world, this is becoming SOP because of a recent change in the UL listing rules for VFDs. VFDs used to be listed under UL508C just like any other electrical power device, but recently UL changed top align with the IEC requirements, and VFDs must now be listed under UL81800-5-1. As part of that change, fuses are now almost always required, even if you have a circuit breaker (it has to do with possible short circuit failure modes of components). But because this will ONLY require fuse protection AFTER something else in the VFD has already failed. they are NOT required to be the Branch Over Current Protection. They CAN be, but it's not required. So when people do not WANT the fuses to be the only thing, because they are super expensive, the drive mfrs are testing and listing the drives with the MAXIMUM size fuses allowable in the NEC, then purposely size a breaker closer to the input amps of the VFD, specifically so that the breaker should trip FIRST, rather than wait for the expensive semiconductor fuses to clear.