GerryB
Senior Member
- Location
- woodbridge, ct. USA
I've been told fuse adapters or reducers are only listed for temporary use, therefore you cannot install 20 amp fuses in a 60 amp service rated disconnect for solar installs. Any one have this issue?
That's not what he is talking about. Most switches will accommodate fuses without reducers from the same as the switch rating down only to the next size up from the rating of the next size switch down , i.e., 70A - 100A fuses will fit a 100A switch but not 60A fuses.Well who told you this? There are millions of 60 amp disconnects with smaller fuses...I don't have a Bussman Yellow SPD catalog but a call or online to bussman would clear this up.
Otherwiser bussman would only sell fuses in standard sizes 60, 100, 200
I've been told fuse adapters or reducers are only listed for temporary use, therefore you cannot install 20 amp fuses in a 60 amp service rated disconnect for solar installs. Any one have this issue?
Whenever that happens we just 40A fuses and conductors.Whoever (wrongly) told you that, ask them to provide documentation. Or show them the reducer documentation. For example this Bussman catalog sheet says nothing about that whatsoever.
This is a common situation for small PV supply side connections where the AHJ wants a 60A disconnect for conductors connected directly to the service conductors. I've done a number of these without ever having heard anything like that.