Here is an interesting possibility. I didn't even know such a thing existed until I looked.
A2D-R - Reducer Fuses - Class RK1 - Time-Delay Fuses | Mersen
ep-us.mersen.com
That document includes the following statement:
"Replaces traditional
temporary-use only Fuse Reducer accessories"
There was an attempt to in a code rule that said that, but it was rejected. Some fuse reducers are listed products and the code change was rejected because the listing standard does not say that they are only for temporary use. As I recall it was Mersen who submitted the PI for this change, and it is interesting that they do manufacturer UL listed fuse reducers.
The following part numbers are the Bussmann fuse reducers that are UL listed.
213, 213-R, 216, 216-R, 226, 226-R, 242-R, 2621, 2621-R, 263, 263-R, 2641, 2641-R, 2642, 2661, 2661-R, 2662, 2662-R, 2664, 2664-R, 616, 616-R, 626, 626-R, 642-R, 663, 663-R, SA, SA
It appears that either 242-R or 2642 would be the fuse reducer needed for this application.
Bussmann also has other fuse reducers that are not listed products.