titan1021
Senior Member
- Location
- Northern California
I am installing a 75kva transformer to provide 200amps to a lighting panel, primary 480v, secondary 208y/120. I've got everything figured out regarding the transformer installation and requirements. However, I've run into a snag. I need to run a 125a sub-feed from the 200a panel but apparently standard BR breakers in 3-pole max out at 100a. I really don't want to get into a panelboard and molded case breakers if possible for the one larger sub-feed I need. The only solution I've come up with at this point would be to install a 125a fused disconnect to feed the sub-panel which is appox. 16ft away on an opposing wall. Just wondering if anyone has a different suggestion or see any issues with my approach.
Thanks.
Thanks.