electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
This topic is headed to left field with opinions...
The combined OCPD rating of taps off the transformer cannot be more than 125% of 75000/(208*(Sqrt3))=260.A Table 450.3(A) note (2) 2002 NEC
If a single tap is terminated in a disconnect of less than or equal to the above you can come off the disconnect with what ever amperage you want to how ever many disconnects/panels other BS you want....
*provided all other rules are followed
I believe that everything that has been said has been fact not opinion. Lets recap: Primary protection for the transformer is always required. Depending on the size of that primary protection, secondary protection may or may not be required. Most/all of the installations I have done and most of the installations I have seen do not require secondary transformer protection because the primary protection is not greater than 125% plus next size up (perhaps my experience can be construed as opinion). I dont see any disadvantage or lack of flexibility in having multiple sets of transformer secondary conductors. For the case where secondary protection is not required, there is no restriction on the number of sets or the sum of the sizes of the OCPD's at the terminations. Where secondary protection is required, we are allowed 2-6 OCPD's and the sum cant exceed the size of a single OCPD - which is 125%+next size up. So for the OP, 208A*1.25=260A. That is not a standard size, so I can use a 300A single OCPD OR multiple devices that add up to that.
Note that we can use next size up for the 450 provisions, but not for the conductors themselves.