I think 240.22 says it all:
"240.22 Grounded Conductor:
No overcurrent device shall be connected in series with any conductor that is intentionally grounded, unless one of the two following ...."
(I left out the unless because I don't think they apply, but please look up the paragraph and judge for yourselves).
Correct me if I'm wrong, but I think "intentionally grounded" would include both neutrals and EGC's and GEC's and other flavors.
Steve