Fused Neutrals
Fused Neutrals
The only place I'm aware of where fusing the grounded (neutral) conductor is prohibited is in service equipment disconnects. Branch circuits are permitted to have the grounded conductor fused. Next question is....why? I've seen installations where a fuse is installed to protect the grounded conductor serving specific types of equipment based on maunfacturer requirements. In the case of a 277v equipment branch circuit that shares a "neutral", there exists a possibility of a lost neutral resulting in the potential of 480V to the equipment. The fused neutral will not limit the voltage, but may provide some protection depending on proper fuse sizing. Best to install dedicated neutrals to the equipment in your installation.