Fuses Blowing on Hermetic Refrigerant Motor-Compressor??

Status
Not open for further replies.

fraserjim

Member
Location
Denver, CO
Customer has two HVAC systems. Each system has two compressors. Stage 1 and Stage 2.

We got called in to help troubleshoot Buss LPJ-30SP 30amp. fuses blowing on Stage 1 of both systems. The systems runs at 480 volt (measured 485V). We measured 24.2 amps while the Stage 1 compressor was running.

Manufacturer's datasheet states: RLA of 27.6 at 460volts.

Each system has a Control Panel with a "Power Block". Control Panel is part of the system. The Power Block feeds the two fuse blocks, single-phase monitors, and contactors.

Last month a HVAC service tech. measure 29amps. running and reduced the refrigerant charge by 2lbs. Still blowing fuses.

Vendor has asked if they can upsize the fuses. Manufacturer states that UL will not allow them to upsize.

Since the Control Panel / Fuse Blocks / Fuses are integral to the system, I do not know what ULs rules are for sizing.

Also, I have never seen a compressor pull that close or over its RLA.

Can someone tell me about how UL sizes fuses and any other things to look for??

Thanks,

FraserJim
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It really depends whether the unit has overload protection or not. Generally with smaller HVAC systems the fuses are sized 175% of the nameplate FLA. The unit should have the max fuse allowed. If the unit is blowing the max fuse then I would say there is a good chance there is an issue with the compressor.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I don't think changing the fuse size is in the cards as this is a factory engineered setup and they probably have thousands of them in the field just like it. Sounds like there is something uniuqe to your system. Do they blow on startup or while it has been running for a while? My guess would be possible voltage imbalance or system charge.
 

kwired

Electron manager
Location
NE Nebraska
Customer has two HVAC systems. Each system has two compressors. Stage 1 and Stage 2.

We got called in to help troubleshoot Buss LPJ-30SP 30amp. fuses blowing on Stage 1 of both systems. The systems runs at 480 volt (measured 485V). We measured 24.2 amps while the Stage 1 compressor was running.

Manufacturer's datasheet states: RLA of 27.6 at 460volts.

Each system has a Control Panel with a "Power Block". Control Panel is part of the system. The Power Block feeds the two fuse blocks, single-phase monitors, and contactors.

Last month a HVAC service tech. measure 29amps. running and reduced the refrigerant charge by 2lbs. Still blowing fuses.

Vendor has asked if they can upsize the fuses. Manufacturer states that UL will not allow them to upsize.

Since the Control Panel / Fuse Blocks / Fuses are integral to the system, I do not know what ULs rules are for sizing.

Also, I have never seen a compressor pull that close or over its RLA.

Can someone tell me about how UL sizes fuses and any other things to look for??

Thanks,

FraserJim

I see conflicts, if RLA is 27.6 I would expect to see a minimum suggested fuse of at least 40 amps, and probably even more likely to be 45 or 50 amps.

Can you give us the unit nameplate data, particularly minimum circuit ampacity and maximum overcurrent protection?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree with the others. Appears to be a incorrect application. You might try to talk with a Bussmann rep and then the factory.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I see conflicts, if RLA is 27.6 I would expect to see a minimum suggested fuse of at least 40 amps, and probably even more likely to be 45 or 50 amps.
Unless, as Dennis suggested, there is no OL relay and the fuses are being used as the running OL protection for the motor, not just the OCPD. It's a bad idea, but it is technically acceptable and unfortunately done all the time in the HVAC industry.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Customer has two HVAC systems. Each system has two compressors. Stage 1 and Stage 2.

We got called in to help troubleshoot Buss LPJ-30SP 30amp. fuses blowing on Stage 1 of both systems. The systems runs at 480 volt (measured 485V). We measured 24.2 amps while the Stage 1 compressor was running.

Manufacturer's datasheet states: RLA of 27.6 at 460volts.

Each system has a Control Panel with a "Power Block". Control Panel is part of the system. The Power Block feeds the two fuse blocks, single-phase monitors, and contactors.

Last month a HVAC service tech. measure 29amps. running and reduced the refrigerant charge by 2lbs. Still blowing fuses.

Vendor has asked if they can upsize the fuses. Manufacturer states that UL will not allow them to upsize.

Since the Control Panel / Fuse Blocks / Fuses are integral to the system, I do not know what ULs rules are for sizing.

Also, I have never seen a compressor pull that close or over its RLA.

Can someone tell me about how UL sizes fuses and any other things to look for??

Thanks,

FraserJim

If you can post any other service data on the equipment along with the model # or name plate data would help. There are several other reasons for the fuse blowing other than the electrical line side, such as ambient temperature, dirty coil, overcharge, bad contactor etc.
 

fraserjim

Member
Location
Denver, CO
Thanks for all of the feedback.

Next site visit is on Monday 9/24.

We have a Fluke 1656 power meter at the fuse block logging for this week.

Some responses.

1. Fuses blowing up while running, not on startup.

2. During our initial testing with the 1656 meter, while running, we logged:

VTHD = 5.49%
Voltage imbalance = 0.64%
ITHD = 3.8%
Current imbalance 5.0%

3. Will try to get all unit nameplate data.

4. Ambient temperature probably in mid-70s.

Additional information / comments / questions

Impact of Voltage imbalance?

They has a catastrophic failure of one Stage 1 fuse block. They replaced with Ultrasafe holder so we can't get temp readings on fuses.
We did scan Stage 2 fuse block and it was reading in the 180 degree range and at about 24amps.

I see NEC 440.52 (A) (1) says overload relay at 140% of RLA. So that wouldn't explain why the fuses are 30amp. if being used as OL relay.

NEC 440.52 (A) (3) calls out for sizing at 125%. So an RLA of 27.6 x 125% = 34.5. Do they have to round down to 30amps. or can they round up?

Bad contactor. Since this is happening on multiple systems, a bad contactor is less likely.

I am still questioning why the RLA is so close to the actual measured running current. The manufacturers service techs. don't seem to be concerned. Is this normal to run at almost 90% of the RLA?

I am still wondering about UL vs. NEC in determining fuse sizing?

Thanks again.

Jim
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Thanks for all of the feedback.

Next site visit is on Monday 9/24.

We have a Fluke 1656 power meter at the fuse block logging for this week.

Some responses.

1. Fuses blowing up while running, not on startup.

2. During our initial testing with the 1656 meter, while running, we logged:

VTHD = 5.49%
Voltage imbalance = 0.64%
ITHD = 3.8%
Current imbalance 5.0%

3. Will try to get all unit nameplate data.

4. Ambient temperature probably in mid-70s.

Additional information / comments / questions

Impact of Voltage imbalance?

They has a catastrophic failure of one Stage 1 fuse block. They replaced with Ultrasafe holder so we can't get temp readings on fuses.
We did scan Stage 2 fuse block and it was reading in the 180 degree range and at about 24amps.

I see NEC 440.52 (A) (1) says overload relay at 140% of RLA. So that wouldn't explain why the fuses are 30amp. if being used as OL relay.

NEC 440.52 (A) (3) calls out for sizing at 125%. So an RLA of 27.6 x 125% = 34.5. Do they have to round down to 30amps. or can they round up?

Bad contactor. Since this is happening on multiple systems, a bad contactor is less likely.

I am still questioning why the RLA is so close to the actual measured running current. The manufacturers service techs. don't seem to be concerned. Is this normal to run at almost 90% of the RLA?

I am still wondering about UL vs. NEC in determining fuse sizing?

Thanks again.

Jim


Do you happen to remember the brand of equipment, Trane Carrier, York etc? Tonage, 10, 12, 20, etc?
 