jmbs
Member
- Location
- marion nc usa
I've done a lot of installs but not a lot of troubleshooting.20 amp brkr to disconnect with 5amp fuses. From disconnect to motor starter with 2.3 amp thermal overloads. 480 volts.2 hp motor on conveyer. All three 5 amp fuses blew today. Replaced fuses runs like new. See if I'm headed in the right direction?- If it happens again I plan to check resistance on the windings and if that checks out meg the whole circuit. For three fuses to bblow that means a dead short right? For future reference, when would overloads kick out before fuses? Thank you for the help.