Fuses or Breakers

I read at that if you use a fuse, it can't be more than 15 amps, But there is no limit for a breakers as long as it protects the conductor, fan motor and inverter. But then I take things literally.
 
I don't think that it's uncommon for someone to use the word fuse when they actually mean overcurrent protection device. You would think that manufacturers would be better at this then everyday people but often they're not. People mix up proper terminology all of the time. How many times have you seen on this forum where someone talks about 15 amp plugs instead of the word receptacles?

Typcially the labeling on this equipment gets lost in translation from a manufacturer in a different country. As electrofelon asked where is the listing agency in all of this? After all they're paid to evaluate this equipment and that should include all labeling.
 
Old school and like to use the lowest ampere time delay quality fuse that will handle the load. For low torque applications such as fans a fuse 125% larger then motor FLA amps always held. On refrigerant & air compressors usually went with 150% of motor FLA. Years ago we had a couple of large centrifuges that you had to hold in a start button for at least halve a minute for them to reach full speed. There were on what looked like a reversing starter. Start starter bypassed the overloads. Had to go 175 to 200 % of motor FLA for fuses. We had over 35 VFD'S that drove 480 volt fan motors with 124 FLA. All had at least a 20 second ramp up time and ones without bypass had 150 amp time delay fuses and ones with bypass 175 amp fuses.
 
I read at that if you use a fuse, it can't be more than 15 amps, But there is no limit for a breakers as long as it protects the conductor, fan motor and inverter. But then I take things literally.
That is an interesting take on it. I would not use more than a 15 amp overcurrent protective device but I hear ya. At our local association zoom meeting one of the members took it that way but I pooh-poohed it.
 