Morning George, i'm sitting in a room @ the Sheraton @ Virginia Beach ,Virginia trying to type this over Web-T.V.,so bear with me... The tap-conductors are the smaller conductors as you have stated,,"tapped from the A/C feeder conductor"..Location of tap,@"LINE_SIDE"of locall outside disconnecting means @ the A/C equipment. Notice of NEC'05 210.63 "shall be" installed @ an accessible location "for the SERVICING of the A/C EQUIPMENT.--the recepticle outlet "shall not" be connected to the "load side" of the equipment disconnecting means..(meaning tap-permitted) .... Refering to 210.19(4)(c) Quote: other than receptacles.. The in-line fuse holder,,violation of 240.10 Supplemntary overcurrent Protection..
Tap Conductor.@ 240..21 (b)(1) ten-foot tap rule. As far as the overcurrent protection of the smaller tap-conductor (the smaller wire)..Take notice of 240.21(b)(4) Quote: For field installations where the tap-conductors leave the inclosure or valt in which the tap is made,,the ratingof the overcurrent device on the line side (AKA. a/c feeder breaker @ panel where feeder recieves supply)-shall not exceed 10 (ten) times the ampacity of the Tap-conductors-(aka.-the smaller wire as you have said)
George,therein lyes the overcurrent protection for the receptacle device for the "servicing factor" alone of the A/C equipment as I have stated.
*this whole installation in original post,...Violation,non-conforming.. (tuff-typing this on web-tv..,not recommended) later...dillon.. .