bmore12586
Member
- Location
- rochester new york
I am using a ABB drive part number is dcs800-s02-0350-05. My situation is i have a 93 KVA 460vac to 240 vac transformer. I have primary fuses which are 150 frs-r and fwp-500 on the secondary. The secondary fuse sizing comes from ABB and these are semiconductor fuses. The ABB documentation tells you to run 500 mcm or parallel 250 mcm on the secondary and the armature wiring for the motor. They are telling you to run a wire size to cover these fuses. The fuses are only sized this way to handle the in rush. My transformer can only put out 234 amps at 240 vac and the drive has a max output of 350 amps DC. Why do i need to run a wire size to cover these fuses when the only time it will ever see the 500 amp load is in a short circuit condition. In my mind i should be ok with sizing wire to the 350 amps dc. I believe that ABB is assuming that there is not any fusing on the primary side. Does anybody have any input and which code would this be handled under.