Second the conductors between the transformer secondary fuse must have an ampacity equal to or greater than the rating of the fuse. The "round-up" rule in 240.4(B) does not apply to these conductors, so the 500kcmil conductors are not large enough for the 500 amp fuses.
Is the transformer a 3 wire to 3 wire delta/delta transformer? Is so, you could use the primary OCPD to protect both the primary and secondary transformer windings as well as the secondary conductors as long as you size the conductors per 240.21(C)(1).
Suppose the transformer is a topology (1-phase or 3Wdelta-3Wdelta) that allows the primary OCPD to protect the secondary wires by proxy, yet there still is an OCPD on the secondary for other reasons. Do you still need to size the wire to the secondary OCPD, even though the wires are otherwise considered protected when you eliminate the secondary OCPD?