Frank A
- Maracaibo, Zulia, Venezuela
I'm calculating the size of a main breaker for a dwelling unit panelboard. I've found that after adding all the load currents with their respective protection factor, the total must be multiplied by 133% for "future capacity".
So, 89.96A * 133% = 119.65A, as per 240.6 the breaker to be installed should be a 125A Inverse-time CB.
Is that true?
If so, which NEC article says so?
Is that true?