FWIW, in the Soares book on grounding and bonding, p 131 it states in regards to using an 8 AWG grounding electrode conductor protected by metalic armored cable:
"The need for bonding the metalic armor or such cable is required in 250.64(E). Where that bonding procedure is not followed, the impedence of the grounding electrode conductor is approximately doubled with the result that its effectiveness is markedly reduced."
The paragraph before this talks about bonding both ends of a GEC to a ferrous metal raceway. (I've noticed in several spots that the authors of Soares, as with the NEC, don't follow good writing practices and a statement of fact, like the one above, which really apply to several examples cited, is placed such that a person could think it only applies to the last example.)
I think what they're saying is that failure to bond reduces the ability of the GEC to effectively conduct fault current. By half, if 'impedence...is doubled'?
Perhaps Larry of Charlie could comment on this.