Yes, unless the 90 is covered with 18" of earth or 2" of concrete. 250.86 Exception #3. As far as how to do it, there is no good way.Do I have to bond, and how do I when using galvanized 90's with pvc pipe.
That is the easy part. Where and how do you run the bond wire?I've never had to bond a 90 like that, but I would probably use a grounding clamp like those used on water lines for services.
It would have to connect to the point where the circuit EGC originates.my only choice would be to run a properly sized bare copper conductor to the grounding grid for the building.
I think that in many cases, that the conductors cannot be installed without damage unless you use a rigid 90.(I think this discussion proves that running PVC above ground with metallic elbows is just not a good idea!!!)
What do you think?
Quote:
(I think this discussion proves that running PVC above ground with metallic elbows is just not a good idea!!!)
What do you think?
I think that in many cases, that the conductors cannot be installed without damage unless you use a rigid 90.
don_resqcapt19 said:Steve,
But then we would have an EGC that is not run in the same raceway as the circuit conductors. 300.3(B).
Don
300.3(B) provides for your installation with a reference to 250.102(E). I'm assuming that in the case of isolated rigid 90's you would not be able to comply with the 6' maximum length in 250.102(E).How would you apply 300.3(B) when I bond two raceways together where I have flex between them at the building expansion joints?
There is an exception, but it is limited and only applies at outside poles.But 2501.102E does provide an exception where you aren't limited to 6', and I think it applies to just these cases.
DonException: An equipment bonding jumper longer than 1.8 m (6 ft) shall be permitted at outside pole locations for the purpose of bonding or grounding isolated sections of metal raceways or elbows installed in exposed risers of metal conduit or other metal raceway.
There is an exception, but it is limited and only applies at outside poles.
You can use metallic raceways and eliminte the bonding problem.Otherwise, we have the lesser of two evils: Either ignore the bonding completely, or pretend there is a pole where there isn't one.
Plant specs where I am at require both an internal EGC and and external bonding jumper for the sealtight.Most motors have a ground connection provided inside the box as well as most combination starters. It would be more cost efficient to run wire internally in this example.
Flexible metal conduit is permitted in Class I, Divison 2 locations. 501.10(B)(2)(2).Now above they talk about hazardous locations, but the flex they are showing I do not think is approved for any hazardous location.
Plant specs where I am at require both an internal EGC and and external bonding jumper for the sealtight.