Am I looking at this correctly... (2017)
210.11(C)(4) requires a dedicated 20 amp circuit for garage receptacle outlets (exception allows accessible outdoor receptacles)
210,62(G) stats that the receptacles in (G)(1) through (G)(3) will be in "addition to receptacles for specific equipment"
210.52(G)(1) requires each vehicle bay to have a receptacle outlet not more than 5-1/2 ft off the floor.
It appears when you install the 20 amp garage circuit and feed the required vehicle bay receptacle that you can not also supply the garage door openers as they are "specific equipment" so they will be required to be on some other circuit (perhaps with garage lighting) but being garage receptacles they would still need to be GFCI.
right ??
210.11(C)(4) requires a dedicated 20 amp circuit for garage receptacle outlets (exception allows accessible outdoor receptacles)
210,62(G) stats that the receptacles in (G)(1) through (G)(3) will be in "addition to receptacles for specific equipment"
210.52(G)(1) requires each vehicle bay to have a receptacle outlet not more than 5-1/2 ft off the floor.
It appears when you install the 20 amp garage circuit and feed the required vehicle bay receptacle that you can not also supply the garage door openers as they are "specific equipment" so they will be required to be on some other circuit (perhaps with garage lighting) but being garage receptacles they would still need to be GFCI.