Where is it stated in the NEC that residential garage door openers must be supplied by a dedicated 20amp circuit?
Nowhere. The NEC doesn't have such a rule. What makes you suspect that there is an NEC rule about this?Originally posted by scnkapc: Where is it stated in the NEC that residential garage door openers must be supplied by a dedicated 20amp circuit?
Why?Originally posted by 110.12:
Your inspector may require a dedicated single receptacle rather than a duplex if it's not on with the GFI.
if someone is going to get a ladder to plug their drill into this receptacle to avoid a GFCI, more power to them. they would also drag an extension cord into the house to acheive this if the garage door opener receptacle was not there. We can not protect idiots.Originally posted by 110.12:
Single receptacle might keep owner from from?plugging in his drill etc into a non GFCI.
As Scott says, 210.8(2)Exception No. 1 to (2): would be the applicable section in this caseOriginally posted by 110.12:
210.8 exception 2 single receptacle.
Roger210.8 Ground-Fault Circuit-Interrupter Protection for Personnel
(2)Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use
Exception No. 1 to (2): Receptacles that are not readily accessible.
The NEC does not directly require any of those items to have dedicated circuit.Originally posted by scnkapc:
I don't get it? If dishwashers, disposals and jacuzzi's have to have their own circuit why shouldn't garage door openers? It is in fact a motor and/or a fixed appliance. Whether it is a 15amp or 20amp, it is still a motor load situation and should have its own circuit!
Must it have its own circuit? No, not by any NEC requirement. Should it have its own circuit? That is a design choice. For a dishwasher, and maybe for a disposal, a separate circuit would probably be a good idea. For a garage door opener, I think a separate circuit would be a waste of a breaker and a waste of wire. It is not a bad thing, if the owner wants to pay for it.Originally posted by scnkapc: . . . it . . . should have its own circuit!
Was it at your own home? If so, did it give you a large number of nuissance trips? If it was not your own home, did you go back and inquire of the owner whether it give him or her a large number of nuissance trips?Originally posted by peter d: I once connected a disposal and dishwasher to the same 15 amp circuit. . . I did it and if felt great!