Under the 2011 NEC, are dwelling GFCI receptacles permitted to be installed in a 9' garage ceiling for a garage door opener? IMO that does not meet the requirement for them to be readily accessible.
 

480sparky

Senior Member
Location
Iowegia
Although no height is mentioned in 210.8, I'd say a 9-foot ceiling would not be readily accessible as defined in Art. 100.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
No, and I agree, in that order. Sounds like there is a need for a proposed revision for 2014. :happyyes:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Under the 2011 NEC, are dwelling GFCI receptacles permitted to be installed in a 9' garage ceiling for a garage door opener? IMO that does not meet the requirement for them to be readily accessible.
IMO, no it is not readily accessible in the ceiling as you need a ladder to reach it.

We install a dead front gfci on the wall in the garage and then feed the overhead door.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No, and I agree, in that order. Sounds like there is a need for a proposed revision for 2014. :happyyes:

I agree, it's pretty stupid as written but what would you propose? A maximum height? I can probably reach the test button on a device in an 8' ceiling. Short inspector maybe only good for 7'. ;)
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
I would have never thought about this ( I don't do very many new homes or complete re-wires) but the last time this came up, I was able to install a GFCI on the garage wall that fed the receptacle for the garage door opener.

I'm not sure I understand why a garage door opener needs to be on a GFCI circuit. I've watched that Youtube video about the kid who got electrocuted by a puddle near the garage but I don't remember thinking that a GFCI would have saved him.
 

jumper

Senior Member
AFAIK, the receptacle only needs GFCI protection, so while the requirement of a GFCI receptacle being readily accessible would seem to to preclude installing one at 9'- it does not say that GFCI protection is not necessary for a garage receptacle at that height .
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Theres nothing that requires a residential garage door to be on a circuit by its self, so I do like others have stated, and just loop it off the wall receptacles.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
We just feed the garage doors off of a GFCI on the wall. So if by chance it does trip they can reset it easily :)

Theres nothing that requires a residential garage door to be on a circuit by its self, so I do like others have stated, and just loop it off the wall receptacles.

Again read the article I post above. If you have two garage doors that draw 6 amps each you cannot have it on with the recep. in the garage.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
How much current do GDO's usually draw?
Some 6 amps but the concept is ridiculous because the current draw on them is for less than 20 secs. I have tried to write a proposal for this but I can't figure it out. I am not sure what section to add it to. We have one area around here that will reject it based on 210.23
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I suspect you only need the nameplate but if you had to use 430.248 a 1/2hp is 9.8 amps-- in reality that is not close.
 