I don't use 14 ga, so it's not a problem on the houses I wire.
Well that is just silly
I don't use 14 ga, so it's not a problem on the houses I wire.
I just looked at the really old cheap junk GDO I have and it is 1/3hp- 6 amps
Well that is just silly
6 amps X 2 is 12 amps-- it is more than 50%. With one door you are fine. Again mine was an old door opener.I don't use 14 ga, so it's not a problem on the houses I wire.
6 amps X 2 is 12 amps-- it is more than 50%. With one door you are fine. Again mine was an old door opener.
I have also done homes with 3 GDO. It can be ridiculous if they are 7 amps and you need 2 circuits for something that is on for a few sec.
Yes , of course, but the posters were talking about using a standard gfci on the wall in the garage. IMO, that make 210.23 active and the install non compliant- this is why you must use a dead front.Couldn't you supply the two doors with one 15 amp circuit but nothing else?
6 amps X 2 is 12 amps-- it is more than 50%. With one door you are fine. Again mine was an old door opener.
I have also done homes with 3 GDO. It can be ridiculous if they are 7 amps and you need 2 circuits for something that is on for a few sec.
Well that is just silly
It is fastened in place -- it still can be cord and plug connected.It's cord and plug connected, not hardwired, also it is a non-continous motor load. It can also be calculated as a motor feeder.
I'm not saying anything is wrong with wiring a house with #14, but #12 is a better quality job, and that's what my customers want, not the run of the mill romex yanker. (And their willing to pay for better quality too)
I'm not saying anything is wrong with wiring a house with #14, but #12 is a better quality job, and that's what my customers want, not the run of the mill romex yanker. (And their willing to pay for better quality too)
I still have yet to see anyone actually quantify how an all #12 house is 'better'.
1. Less voltage drop
2. Higher available circuit capacity
3. Higher resistance to failure from physical damage
Just to name a few
I still have yet to see anyone actually quantify how an all #12 house is 'better'.
So why not use #10? If 12 is so much better, 10 would be that much closer to nirvana.
Less voltage drop...... assuming the same number of outlets per circuit. Most don't wire with 12 that way. They use less circuits.
Higher circuit capacity... again, falls apart when you add more loads to less circuits.
Higher resistance to physical damage? Huh? Someone actually tested how much force it takes to damage 14 compared to 12? Where's the stats on that one?
......... The higher resistance to damage comes from when your helper nicks a #14 when they strip it, it will break at that point much easier than a #12 with the same nick.