bark

Member
Location
Washington
Been awhile since I wired a garage. Do all recepts have to be GFCI protected or can there be designated recepts for appliances? This is for a residence.
 

mwm1752

Senior Member
Location
Aspen, Colo
  1. Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit interrupter protection for personnel.
(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use
 