I got gigged once for using conduit to protect some romex for a short (3') run to get to a wall as the conduit derates in size so much with "insulated wires". Does this still apply to a short sleeve thru a stud or joist?
For a 3' piece you may be able to apply 310.15(A)(2)Exception. This would require a minimum circuit length of 30'. If you had 30' or more then no derating would apply.