1stYearElectrican
- Newfoundland, Canada
Folks, I need a lil help in a question if you be so kind. I feel I know the answer BUT according to journeyman it was labeled it ok, Here is the case:
Installing a sub panel in a garage from the main panel in house. The conductors supplying the sub are thru PVC underground. The sub-panel is 100A and the main panel in house is a 200 amp service.
Here is what I believe is wrong, the conductors running thru the PVC and powering the sub panel are #4 AWG XPLE ALUMIMUM 300V. According to the tables this conductor is rated at 80-90 AMPS and will be supplying a 100A panel. These conductors can not handle 100A. Am I correct in this??
A friend of my Brothers from the power company gave him several hundred feet of #4 AWG XPLE ALUMIMUM 300V and assured him that it was ok to use it to supply a 100A panel. And on top of that an electrician also gave him the ok to use it. Is this really ok??
What i figured is that a #3 COpper awg would suffice or a bigger awg ALUM conductor to supply a 100A panel.
Is the power company guy and electrician right or do I need to do more deeper reading in the code?
The Panel will supply 8 floricent(spell?) lights, a 50 AMP welder and a oil/wood burner furance, 10 recepticles, 3 outdoor lights and a garage door opener.
Thanks
~FyE~
Thanks
~FyE~