Hi
I am wondering about table 300.5
If a 2-00 amp feeder is in PVC SCH 40 and running under garage slab which is at least 4 inches of concrete, how deep the conduit should be? Table says no vehicular but garage slab is under one or 2 cars? If the conduit continues in a driveway which is used by 4 units and it has ASPHALT, then what is the required depth under asphalt? What if we pour 2 inches of concrete on the PVC conduit and fill with dirt and then asphalt? What depth is acceptable?
Abe
 
Last edited by a moderator:
Hi
I am wondering about table 300.5
If a 2-00 amp feeder is in PVC SCH 40 and running under garage slab which is at least 4 inches of concrete, how deep the conduit should be?
Inside the garage you are fine.

Table says no vehicular but garage slab is under one or 2 cars?
Table 300.5 does not apply to a garage.

If the conduit continues in a driveway which is used by 4 units and it has ASPHALT, then what is the required depth under asphalt? What if we pour 2 inches of concrete on the PVC conduit and fill with dirt and then asphalt? What depth is acceptable?
Abe
When you are under a driveway Table 300.5 does apply, encapsulating it in concrete does not give any leeway to this.

Roger
 