It is less then the 32 mentioned in the OP, unless they recently changed those math concepts on me(18) circuits is a lot for a standard detached garage.
JAP>
No they typically don't need much more then a couple circuits, and often just one can get you by.You know they dont need that many out there.....
that when utilizing the "2 thru 6" provision, there not be more than 6 physical spaces in the equipment
Yes I know it does not require a main disconnect just based on number of spaces. However, as soon as you install the 7th disconnect you are in violation.
Some of our local AHJ require a main disconnect if we have more than 6 spaces or if the panel is a 6 space 12 circuit capacity.
NEC isn't worded that way, but I can understand some local jurisdictions amending it to be that way.Yes I know it does not require a main disconnect just based on number of spaces. However, as soon as you install the 7th disconnect you are in violation.
Some of our local AHJ require a main disconnect if we have more than 6 spaces or if the panel is a 6 space 12 circuit capacity.
NEC isn't worded that way, but I can understand some local jurisdictions amending it to be that way.
I don't have as much issue with it for miniature breaker type panels, but I have installed I line panels using the six disconnect rule with all the breakers installed being over 100 amp with left over mounting space but these panels are not the type where someone typically comes along and adds a 15 or 20 amp circuit to just because it is easy to do. In fact the local handyman or maintenance man at the facility probably has no idea how to add a breaker to this panel so that means most of the time someone more qualified will be making the decision to violate the six disconnect rule if it happens.
Some of our local AHJ require a main disconnect if we have more than 6 spaces or if the panel is a 6 space 12 circuit capacity.
I agree - once you have seen it done. First time looking at one if nobody guides you a little you may take a while to figure it out if all you know is the typical miniature plug on style breaker. This series of breaker isn't something you go to local hardware store or even big box and it is on the shelf either, leaving more experienced (and likely more qualified) electrical workers being the majority of those that ever install them.I line panels are easier to add breakers to than most miniature type panels in my opinion.
JAP>