1793
 - Louisville, Kentucky
 - Inspector
I was asked to look at a job with the following:
Detached Garage with underground feed from House
60A 2pole feed, three wire to 12 circuit panel in Garage
Main breaker backfed in Garage
1/2" CU ground rod with what looks like #8 to grounds in Garage panel
Floating neutrals in Garage panel with Grounds bonded to panel
Walls are finished with OSB on walls and ceiling
Second floor of Garage is partially floored with OSB, down the middle
Can see both ends, in the attic, above panel and over 1st two gang
There is a 12/3 romex in the Garage panel feeding two two gang receptacles. Only one of the Hots, the black, is being used with this circuit, Red caped off.
When this circuit is energized there is current on the GROUNDS and I mean ALL the Grounds. The circuit stays energized.
I'm thinking that there must be a nail, screw or staple in the wire touching the Hot & Ground.of the 3 wire.
From the description, does this sound right?