garage

Status
Not open for further replies.

bartman42

Member
is it ok to run a 10" pvc pipe from 1 building to another apprx 12'. house to a garage,then run water pipes and seperate branch circuits for lighting and recepts?
 

mdshunk

Senior Member
Location
Right here.
No...

The violation is not cables or conduits in the same subterranian casing as water lines.

The violation is that you propose to run multiple circuits to a detached structure, when you're only permitted to have one, with a few exceptions. See 225.30 and
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Marc. You'll need to install a subpanel at the garage if you require multiple branch circuits there.
 

Bea

Senior Member
mdshunk said:
No...


The violation is that you propose to run multiple circuits to a detached structure, when you're only permitted to have one, with a few exceptions. See 225.30 and

He might be installing a multiwire branch circuit for the purpose of 225.30 this is only considered a single circuit:smile:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If the conduit is below grade you would have to run cable that is UG listed. In our area you must use UF cable if a conduit is used as a sleeve below grade. Below grade is considered outside the building and thus must be listed for wet areas. I know that nm cable has thwn in it but the jacket is not listed fot the use.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Dennis, I'm going to pick your post apart, advance warning. :D
Dennis Alwon said:
If the conduit is below grade you would have to run cable that is UG listed.
Not by the NEC. See 300.5(B), they are required to be listed wet.

In our area you must use UF cable if a conduit is used as a sleeve below grade.
For it's wet listing, or direct burial listing? You can use THWN in conduit, right?

Below grade is considered outside the building and thus must be listed for wet areas.
Not all outside areas are wet, some are damp. 300.5(B) works to eliminate any confusion by requiring all underground installations to contain conductors listed for wet locations.

I know that nm cable has thwn in it but the jacket is not listed fot the use.
There has been a lot of discussion about what the conductors are inside NM cable - do you have a document that clears this up, or are you taking an educated guess like the rest of us? ;)

I agree with your main principle, that since NM is not listed for wet locations, it is not permitted to be used underground, by 300.5(B).
 