If the garage is not attached to the house to set a sub-panel in it with no water in garage do you treat it as a new service? and do you need 2 ground rods?
2008 code you need a 4 wire feeder, a main disonnect and 2 ground rods. The GEC from the ground rods get connected to the ground bar in the sub. The neutral is isolated from the ground,.Texhunter7 said:If the garage is not attached to the house to set a sub-panel in it with no water in garage do you treat it as a new service? and do you need 2 ground rods?
Texhunter7 said:O.k. was not for sure on it but you still float your neutral at the panel garage from what i understand from what was said?
If all they want is 2 circuits then you can run a 10/3,12/3 or 14/3 uf with ground and and use a dp switch as your disco to feed the outlets and lights. No ground rod or panel needed. Art.225.30-- last sentenceTexhunter7 said:The garage is already built they just want power to the garage for outlets in the garage.
I think I don't like metal conduit underground. It eventually returns to Mother Earth.brother said:What do you think??
brother said:What do you think??