IMO, No............................................
Isn't that only if it's a receptacle outside the kitchen?Unless it is within 6' of the sink.
No. For awhile the code required GFCI protection within 6' of a sinkcorrect
Yes but it didn't measure the distance thru doors.No. For awhile the code required GFCI protection within 6' of a sink
Ron
That is exactly correctRon, I believe in 2011 the 6' requirement was for other than kitchens.
(7) Sinks — located in areas other than kitchens where receptacles
are installed within 1.8 m (6 ft) of the outside
edge of the sink
Yes. 2011 kitchen gfci requirement was for countertop only.Ron, I believe in 2011 the 6' requirement was for other than kitchens.
210.8(a) (6). 2011 nec . receptacles installed for disposals, dishwashers, trash compactors, are not required to be protected by GFCI.That is exactly correct
They are if they are installed somewhere other than a kitchen and they would have to have a really long pipe connecting them to the sink not to be.210.8(a) (6). 2011 nec . receptacles installed for disposals, dishwashers, trash compactors, are not required to be protected by GFCI.
Well, in dwelling units it covers all receptacles in a kitchen (not just the countertop, a change from 2020) and any receptacle within 6' of a sink, with the distance measured through cabinet doors.I find it odd that the 2023 requires microwaves to be gfci protected but not garbage disposals connected to a sink