2023 NEC Quiz question:
Is there one answer for individual circuits and another for two or more loads on a circuit?
If its on a individual circuit then B is correct, but if its on a circuit with two or more loads the you use A?
What do you all think?
table 430.248 has 3/4HP = 13.8A X 120V = 1656 VAA garbage disposal is to be wired with a nameplate that says 9.5 A , 3/4 HP, 120 volts.
What is the calculated load of this disposal on a branch circuit with two or more loads according to article 210?
A) 1656 VA
B) 1140 VA
C) None of the above
What is the calculated load for the disposal on a individual circuit according to 422.10?
A) 1656 VA
B) 1140 VA
C) None of the above
Is there one answer for individual circuits and another for two or more loads on a circuit?
If its on a individual circuit then B is correct, but if its on a circuit with two or more loads the you use A?
What do you all think?