250.53 D. My understanding is that just because it is there does not mean that it has to be used.
My understanding Is that I have several options for the GE system.
If I had building steelI would use it is my main electrode and the supplement with a ground rod.
On a residence, I am just going to drive 2 grounds. This satisfies 250.53.
Bonding 250.104 A 1 does say that the water pipe must be bonded. If it is pex, then obviously not.
Now here in OKC, we have been required to bond the gas pipe and according to Mike H the mechanical code requires the gas to be bonded with a #6.
Since the 250.104A1 would require the water pipe to be bonded with a number, could I just bind the gas with the #4 since it is closest to the service and at the other end where the water heater is with 3 pipe clamps to cover the hot side install a #4 jumper from the gas to the water at the water heater?
I still contend that does not meet 250.104(A)(1):
(1) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to any of the following:
(1) Service equipment enclosure
(2) Grounded conductor at the service
(3) Grounding electrode conductor if of sufficient size
(4) One or more grounding electrodes used, if the grounding electrode conductor or bonding jumper to the grounding electrode is of sufficient size
Bonding the water to the gas is not listed as the gas piping is not a (1)-(4) allowable point.