Gas Cooktop GFCI?
Bama_Electrical
Alabama
I have a customer that is replacing their induction cooktop which was hardwired to 240v. They are reaplcing it with a Gas Cooktop that is 120v. It plugs directly into a dedicated 15A receptacle. I included the instructions here. Curious if the receptacle is required to be GFCI per code. The receptacle will be located in the cabinet below the cooktop.
Code says that GFCIs are required for all countertop outlets, or any outlets within 6 feet of a sink.
Even if it is within 6 feet of a sink, I would not install a GFI because it is installed inside the cabinets
Is the 6' requirement for the range or for the receptacle?
Well the cooktop is more than 6' you are fine but I should have been clear that the 6' is from the receptacle which makes no sense. If the appliance is close to the sink then you would think you want to protect the appliance as well as the receptacle.
Yeah, stupid!
But, we all can make a list. Can't we?
Yeah, stupid!
They corrected that in the 2023 code for sinks in other than dwelling units, as the measurement is now from the appliance and not the receptacle.
For dwelling unit kitchens, they removed the issue by requiring all receptacles in the kitchen to have GFCI protection.
You know, I figured that would happen in the 2023 code. Thanks for the update.
Ron
So the measurement is to the receptacle for a refrigerator, but to the cooktop from a sink. Nice consistency.
No. In the 2020 code the measurement is from the sink to the receptacle in 210.8(A) and 8(B).
In the 2023 code the requirement is that all receptacles in a dwelling unit kitchen have GFCI protection. The rule is still for receptacles within 6' from the sink for sinks not in a kitchen.
However the rule 210.8(D) for specific appliances has been expanded to include additional appliances. This rule requires that the outlet that supplies any the listed appliances must have GFCI protection and that applies to both dwelling and non-dwelling occupancies. List items (8) through (12) are new for the 2023 code. The previous code just referenced 422.5(A) that only includes the first seven list items. Note that this rule does not say receptacle....it says outlet.
The list is:
1) Automotive vacuum machines
(2) Drinking water coolers and bottle fill stations
(3) High-pressure spray washing machines
(4) Tire inflation machines
(5) Vending machines
(6) Sump pumps
(7) Dishwashers
(8) Electric ranges
(9) Wall-mounted ovens
(10) Counter-mounted cooking units
(11) Clothes dryers
(12) Microwave ovens
The list is:
(6) Sump pumps
(7) Dishwashers
(8) Electric ranges
(11) Clothes dryers
Don, have there been documented cases where the lack of gfi protection has led to serious issues or is this just part of the continuing trend of changes without documentation?