A mechanical engineer I'm working with seems to believe that the fuel supply for an EMERGENCY generator cannot be natural gas, but that it's fine for a STANDBY generator. I'm looking through NFPA 110 and can't seem to find anything that states this. It mentions gas-fired prime movers, but are they talking about natural gas or liquid gasoline? If there are any other codes that might disallow natural gas fired emergency generators let me know so I can look into it but I don't believe it to be the case. Thanks.
The basic issue as pointed out is a question of what specific events are you trying to plan for. In many areas the possibility of losing both electrical power AND natural gas simultaneously may be low while for others it may be quite high. If that is not an issue then long term maintenance on a natural gas generator is a lot less painful.
The second issue is that of standby vs. emergency generators. A standby generator can be as simple as one that you go down to the local hardware store to purchase and plug into it. An emergency generator has a number of requirements such as an automatic transfer switch, automatic or manual testing/exercising, and so forth. A standby generator really has very minor requirements and you can implement as many or all of the features that you get with an emergency generator except one. You cannot use short-circuit only protection with a standby generator. Overload protection is required. One could argue the idea that being able to run an emergency generator for just a few more minutes while the generator coils, feeder cables, etc., are burned up and destroyed while the load itself melts from pulling too much current under a low voltage condition, but on an extremely theoretical basis the whole idea is to provide backup power in an emergency at any cost.
So from a practical point of view you can simply implement the generator as a standby generator and do absolutely everything that the emergency generator rating gives you save the ability to skip out on some electrical protective relaying, or you can go the emergency generator route and deal with all of the additional requirements.
This is akin to putting in emergency stop buttons that have a lot of Code requirements under OSHA as opposed to putting in "Stop" buttons that do exactly the same thing and have no special regulatory status and are completely optional except for one special case (presses).