kwired
Electron manager
- Location
- NE Nebraska
I can see potential sewage backup into people's homes creating a legally required standby system on some level.
.... if all you legally need is an optional standby generator ...
I can see potential sewage backup into people's homes creating a legally required standby system on some level.
Not well phrased.I am not clear on that, it seems contradictory. Could you clarify?
Not well phrased.
Better would have been:
"If under the NEC your proposed generator would just be an optional standby supply...."
I will agree that it may only require two hours of fuel and if so anything beyond that is an optional design issue.And it may well be, yet is still only required to have two hours of fuel on site.
Sorry if I seem nit picky here, I just think we keep going past what is code required and into design.
I will agree that it may only require two hours of fuel and if so anything beyond that is an optional design issue.
First you can store NG as compressed natural gas at your site and there are compressors available to provide compressed storage. I am not aware of this actually being done. Second take a look at 700.12(B)(3) and its exception.You all went off on a tangent a bit here and I'm not trying to keep up.
If NEC 700 states a minimum of 2 hours of on-site storage, then common sense says NG isn't a viable source because you can't store NG at your site, correct?
Maybe, however if the egress lighting is of the "unit" type, the supply is not an emergency circuit. I think that the codes require the fire alarm to have battery back up and don't think the supply to the fire alarm panel is an emergency circuit, but not 100% sure.Question 2... if I have egress lighting and fire alarm loads on my gen, does that automatically classify it as "emergency"? I think so, so how can that be up to the AHJ?
Maybe, however if the egress lighting is of the "unit" type, the supply is not an emergency circuit. I think that the codes require the fire alarm to have battery back up and don't think the supply to the fire alarm panel is an emergency circuit, but not 100% sure.
Unit equipment, with internal energy storage, does not have to be always on.What do you mean when you says "unit" type? A lighting fixture with an integral battery backup that runs unswitched, almost like a night light?
I think that the codes should be changed to require more fuel for emergency generators, or at least dual fuel capability so they can run off NG instead of relying on a finite fuel source. My understanding is at least one of the hospitals in town only has a few hours of diesel for its gensets.
I think what paulengr is saying is that if all you legally need is an optional standby generator you will be wasting money if you specify an emergency generator instead.