gas company has been called to turn on the meter of an apartment in a 17 unit apartment building. They claim there is 9 volts on gas line and they will not connect the gas. what should be done? bonding to cold water and metal part of electrical meters solve it? Thanks
Rewire the complex for all electric heat and appliances. That'll fix 'em.Hi
This is probably a more workable course of action, and is what I would do. I would also talk to someone higher up at the gas company before I did any extra work...... ask gas tech exactly where, what, how he measured voltage.
Look at NEC 250.52(B). You cannot use metal underground gas piping systems as a grounding electrode. So if you bond it then it will become a grounding electrode.
No it won't.It just becomes a piece of metal that is bonded to an electrical service.
There should be an insulating coupling inside the gas meter that electrically isolates the interior gas pipe from the earth. You must bond on the premises side of that coupling. If you bond on the utility side it will become an electrode and therefore a violation.:happyno:
My point being, if the plumber uses CSST type gas pipe, then I have to bond the gas piping... simple as pie in my opinion.. You are confusing the wording of the NEC, it simply states that you cannot use the gas pipe as a GEC... but if it gets bonded anyway... o'well.
^^^^You say that there was a gas tank in the yard? That means the gas was not coming directly from the gas company but was being stored in the tank instead. Why would there be a gas meter if the owner already has a storage tank for his gas?
The rules of the NEC are very clear about underground gas piping. You cannot use it as an electrode. The only way to bond an interior gas pipe and keep the underground portion of the pipe from developing stray voltage and electrolysis is to have an insulating coupling close to where it enters the building.
Part of my point here is with that kind of voltage seeking a path to earth a dielectric union is not going to stop it.
A dielectric union as you call it will prevent electrolysis. This is what the gas company is concerned about. Here is the NEC rule again:
250.52(B) Not Permitted for Use as Grounding Electrodes.
The following systems and materials shall not be used as grounding electrodes:
(1) Metal underground piping systems
(2) Aluminum
I happen to know that the water companies have the same complaint about using their pipes as electrodes because of electrolysis. Imagine if a gas or water pipe were to become corroded and spring a leak as a result.
^^^^ And what about stray voltage on the gas company's pipeline? Apparently they consider it to be a problem otherwise they wouldn't refuse to turn on the gas.
I do not see the gas company complaining about stray voltage on the premises side because the piping is the property of the owner and not the gas company. If there is no dielectric coupling then the gas company should immediately install one.