NFN but sounds like NEV
NFN but sounds like NEV
OP wanted to bond to water pipe and or electrical service. I mentioned in post #2 first thing is to find the source of voltage. Just bonding it, whether right or wrong, doesn't necessarily make the problem go away - it might just mask the problem.
If there is an intentional bonding on the premises side, and/or there is appliance tool with a case ground that is fed by a gas pipe, wouldn't this mean that the gas pipe would manifest whatever Neutral to Earth Voltage was about. I would see if the voltage is about the same and varies similarly to any measured neutral to earth voltage.
Around here the gas company and the electric company are the same animal so you can tell 'em its their problem.
On the electrolysis thing, every metal pipe water service I've ever seen is grounded to the metal water pipe deliberately on the utility side of the water meter. Out here in the hinterlands we use electrodes cause the water pipe is all plastic.
Admit I'm confused between the portions of the code that seem to say you can't ground/bond to metal piping systems and assertions that you must use metal water piping if present, e.g.:
250.52(B) Not Permitted for Use as Grounding Electrodes.
The following systems and materials shall not be used as grounding electrodes:
(1) Metal underground piping systems
(2) Aluminum
and kwired:
Water companies can complain all they want about current on the lines - it will happen anyway which is one reason why
NEC wants metal water piping to be used as grounding electrode if it is present. Water piping will usually have lower resistance than any made electrodes - that is just the way they naturally are.
now the second contention doesn't have citation, but it jibes with every urban installation I've ever seen.
I also see that it is ambiguous whether what 250.52(B) is saying is that you have to install a separate electrode or you cannot bond to metal underground piping systems.
I think this worthy of fleshing out some more.
thanks,
brian