LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
And, had the water heater's supply (i.e., the circuit likely to energize the piping) inlcuded an EGC, the breaker would have tripped.haskindm said:I was called out to check a house one time where the owners were receiving a shock whenever they touched a faucet. Turns out that the Water Heater was faulted (fed with 2-wire romex) and the waterline was NOT bonded.