gas line spark

Merry Christmas
Status
Not open for further replies.

djr363

Member
while removeing a gas union from a furnace, there was a spark (the gas was off), what is the cause of this
 

bob

Senior Member
Location
Alabama
Re: gas line spark

The gas pipe is either making contact with the water pipe or it has intentionally been bonded to the water pipe and is acting as a return path for current.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Re: gas line spark

Bootleg/false grounds, (Tiing G-N) at appliance electrical outlets, can also provide objectionable-neutral current paths along anything connected to the case or frame of the appliance, including water, gas lines, or people, if those lines make contact with main bondings or earth.
 

mark480

Member
Re: gas line spark

Bob, your comment is the reason why many electricians are uncomfortable with bonding the gas line to the grounding electrical conductor or water pipe, article 250.104 I am not disagreeing with you, I find that electricians have different opinions on this sub. I would like all of yours .thanks
 