hurricaneflyer
Member
If gas pipe bonding is to be sized according to the size of the circuit that might energize it, could a grossly oversized gas pipe bonding conductor cause the pipe to become part of the grounding electrode system reguardless of any good intensions? If the grounding electrode conductor and the gas pipe bond are the same size, and are terminated at the same place in the service panel then a buried gas pipe would carry the same or more current than the grounding electrode in case of fault or lighting strike?
If gas goes to three appliances, the size of the bonding conductor would be based on the size of the largest appliance circuit, based on the idea that it is not likely more than one of the appliances will cause a fault at the same time? In other words dont total up all the appliances that could energize the gas pipe?
In this instance I cant just use the appliance ground, it is new construction and the inspector wants the bond installed at rough in.
It seems obvious I am not understanding something.
If gas goes to three appliances, the size of the bonding conductor would be based on the size of the largest appliance circuit, based on the idea that it is not likely more than one of the appliances will cause a fault at the same time? In other words dont total up all the appliances that could energize the gas pipe?
In this instance I cant just use the appliance ground, it is new construction and the inspector wants the bond installed at rough in.
It seems obvious I am not understanding something.