?G2411.2 (310.2) Gas pipe bonding - systems that contain CSST. A gas piping system that contains any corrugated stainless steel tubing (CSST) shall be electrically continuous and shall be bonded to the electrical service grounding electrode system at the point where the gas service enters the building or structure. No portion of the gas piping system shall be used as or considered to be a grounding electrode or a grounding electrode conductor. CSST shall be installed and bonded in accordance with this section G2411.2, and the stricter of: (a) the requirements set forth in the CSST manufacturer?s installation instructions, or (b) the requirements set forth in Sections G2411.2.1, G2411.2.2, G2411.2.3, and G2415.5.
?G2411.2.1 Bonding jumper. Where the electric service for the individual installation is 200 amperes or less, the bonding jumper shall not be smaller than 6 AWG copper wire or 4 AWG aluminum or copper-clad aluminum wire, and shall be permanently connected to the grounding electrode system. Where the electric service for the individual installation is more than 200 amperes, the bonding jumper size shall be determined in accordance with Table E 3503.1, and shall be permanently connected to the grounding electrode system.
?G2411.2.2 Bonding clamp. The bonding jumper shall be connected to the gas piping system with a bonding clamp that is listed for the material of the bonding jumper and for the material of the component of the gas piping system to which the bonding clamp is attached. The bonding clamp shall be attached to the gas piping system at a point which is inside the building or structure in which the gas piping is installed, on the downstream side of the gas meter or regulator, in an unconcealed and readily accessible space, and as close as practicable to the point where the gas service enters the building or structure. The bonding clamp shall be attached to a segment of metallic fuel gas pipe which (a) is a component of the gas piping system, (b) is electrically continuous with all CSST components of the gas piping system, (c) is made of steel or wrought-iron, (d) complies with Section G2414.4.2 of this code and with all other applicable provisions of Section G2414 of this code, and (e) is not less than 3 inches (76 mm) in length. Neither the CSST nor the brass hexagonal nut on the CSST fitting shall be used as an attachment point for the bonding clamp.