CuriousHomeInspector
Member
- Location
- Little Rock, AR, USA
Consider the following image:
Others have called this out as improper... I would definitely agree with it isn't a "best practice," but I'm curious what electricians would say about the image.
Assume a few things: 1) 2017 NEC 2) The gas piping meets a requirement to where it needs to be bonded to an equipment grounding conductor, and the conductor in the image is the appropriate size.
I know of nothing specific that states that the connections of a gas appliance connector are not electrically continuous.
Questions:
1) Is the connection between the sediment trap and piping at the appliance considered electrically continuous with the house piping in the photo that it is connected to? Electrically is it treated any differently than any other metal to metal connection?
2) Is this an improper bond/connection (excepting the fact of course that when the appliance is disconnected/replaced the connection would need to be moved etc
Thanks
Others have called this out as improper... I would definitely agree with it isn't a "best practice," but I'm curious what electricians would say about the image.
Assume a few things: 1) 2017 NEC 2) The gas piping meets a requirement to where it needs to be bonded to an equipment grounding conductor, and the conductor in the image is the appropriate size.
I know of nothing specific that states that the connections of a gas appliance connector are not electrically continuous.
Questions:
1) Is the connection between the sediment trap and piping at the appliance considered electrically continuous with the house piping in the photo that it is connected to? Electrically is it treated any differently than any other metal to metal connection?
2) Is this an improper bond/connection (excepting the fact of course that when the appliance is disconnected/replaced the connection would need to be moved etc
Thanks