I agree the intent may not necessarily be to require an 8 AWG ground in this case - but they wrote one rule to fit all situations, and either isn't quite being understood, enforced, etc. or people just don't realize the rule is there, so it hasn't caused enough problems for anyone to submit PI to try to change it.
Like I said upsizing a 20 amp circuit to 8 AWG - the 10 AWG EGC probably is not going to effect performance of OCPD all that much for under 100 feet length. Longer runs it very well could. Available fault current at the start of the circuit also has an impact on real world situation.
NEC just decided proportional increase in EGC was a one size fits all solution.
I understand what you are writing. My point is this: If a #10 ground is fine for #8 ungrounded conductors on a 40A OCPD, then it should be fine on a 20A OCPD. If you need a #8 ground with #8 ungrounded conductors for a 20A circuit, you should need them on a 40A circuit too.
I get that the grounds have to be proportionally upsized when the ungrounded conductors are upsized. The problem is that the sizing required by circuit amperage is not a linear progression. #14 thru #10 hots (small conductors per 240.4) require the same size grounds, but #8 and #6 hots require only a #10 ground wire.
If a #10 ground is good (Code acceptable) for a 60A spa circuit utilizing #6 hots (and it is), it should be good for a 15A circuit doing the same. There's *roughly* 4x less fault current that will flow thru a 15A breaker before it trips than a 60A, so there's no way if a #10 is sufficient to carry the fault current for the 60A spa that it's insufficient for a 15A receptacle.