Ok, so at a gas station/c-store, when running underground conduits to dispensers, sumps, tanks, etc, I recall somewhere in chapter 5 of the nec, it states that bonding of these rigid conduits cannot depend on a double locknut. Basically where my pipes come up beside the building into the gutter. So my questions are:
1.Am I required to use a bonding bushing or bonding locknut?
2.Does this rule change if the conduit run only has stub ups of rigid, and the rest being pvc?
3.If a ground bar is set in the exterior gutter, does my egc from the ground bar to the panel inside need to be larger than what is required for the largest load, no matter the number of points out in the feild?
4.It states that bonding needs to be retained on the circuits back to the service. Does a pvc chase from the exterior gutter to the interior gutter eliminate this since bonding cannot be done on pvc?
Thank you
Duke
1.Am I required to use a bonding bushing or bonding locknut?
2.Does this rule change if the conduit run only has stub ups of rigid, and the rest being pvc?
3.If a ground bar is set in the exterior gutter, does my egc from the ground bar to the panel inside need to be larger than what is required for the largest load, no matter the number of points out in the feild?
4.It states that bonding needs to be retained on the circuits back to the service. Does a pvc chase from the exterior gutter to the interior gutter eliminate this since bonding cannot be done on pvc?
Thank you
Duke