For residential 220v with a 50 amp breaker what is the gauge requirement for the wire? Thanks in advance.

Jim
 
Re: Gauge Requirements

Thanks for your response, I noticed in my parents new home it is wired with 10 is that OK? Dangerous? Please also see my other posts on the lights dimming when the AC comes on could this be the cause?

TIA

Jim
 
Re: Gauge Requirements

If this is for the A/C unit, there are special rules that apply to the wire size and over current protection. As stars said it depends on the connected load, and also on the information on the A/c unit lable.
 
Re: Gauge Requirements

Thanks again. The unit is a Trane the label calls for a 50 amp breaker and has a minimum circuit amperage of 29 amps.

Jim
 
Re: Gauge Requirements

Originally posted by jimdiaz:
Thanks again. The unit is a Trane the label calls for a 50 amp breaker and has a minimum circuit amperage of 29 amps.

Jim
With this being the case, all is fine and per code.

Roger

[ August 08, 2004, 05:55 PM: Message edited by: roger ]
 
Re: Gauge Requirements

I am closing this thread from further discussion because the correct response has been given and further discussion should be between the home owner and his electrician.
 